NCC-2011 (National Construction Code) NSW 3.2.2.6 Damp-proofing membrane
A damp-proofing membrane must be installed under slab-on-ground construction for all Class 1 buildings and for Class 10 buildings where the slab is continuous with the slab of a Class 1 building as follows—
(a) Materials
A damp-proofing membrane must be—
(i) 0.2 mm nominal thickness polyethylene film; and
(ii) high impact resistant, determined in accordance with criteria specified in clause
5.3.3.2(c) of AS 2870; and
(iii) be branded continuously "AS 2870 Concrete underlay, 0.2 mm High impact
resistance".
(b) Installation
A damp-proofing membrane must be installed as follows—
(i) lap not less than 200 mm at all joints; and
(ii) tape or seal with a close fitting sleeve around all service penetrations; and
(iii) fully seal where punctured (unless for service penetrations) with additional
polyethylene film and tape.
(c) The damp-proofing membrane must be placed beneath the slab so that the bottom
surface of the slab is entirely underlaid and extends under edge beams to finish at
ground level in accordance with Figure 3.2.2.3 (also see Figure 3.3.4.9 for single skin masonry details).
Note:
A range of polyethylene films can be used, including black film and orange film, provided they satisfy the requirements for high impact resistance in accordance with the criteria specified in clause 5.3.3.2(c) of AS 2870.
The "Damp-proofing membrane" is there to stop rising damp.
Your PCA had to verify the form-work, re-enforcement etc before the concrete pour. If it so, don't worry about it.
Also, you said "I have a ..." not sure about this "I have" bit